• As of January 1, 2018 The brand new logo that was created and released in 2017 will be the only official logo in affect and allowed to be used on any electronic media however, any such media like truck wraps, stationary, and postcards will be grandfathered in. Contributing Members will be allowed to use the UAMCC logo in any advertising. Permission to use the logo otherwise must be in writing. Logos used in electronic formats (ie: Websites, forums, etc.) must be linked back to the member’s profile in the UAMCC directory. Contributing Members are members that are paid and current with their dues. Please contact info@uamcc.org with any questions.

Parking Garage Cleaning. Issues that may arise from the cleaning.....

There are so many issues that may arise from a Parking Garage Cleaning. I have been asked " What issues can arise in a Parking Garage Setting?"

Boy, is that a loaded question....

Today and Tomorrow ( if I have time ) I will try to submit two areas of Garage Cleaning that I have not witness being discussed since I have been on the boards almost 1.5 years now. Many have asked, only a few know the answer !
 
One issue is the Fire Sprinkler Systems.....

Sprinkler heads, other than ornamental or plated heads, should be color coded, as outlined in NFPA 13, subsection 6.2.5 . The color identification may be by a single dot on the deflector, painting of the toggle arms, or for bulb type sprinklers, the color of the glass bulb.

The Color-coding by the temperature-classification is as follows....

Ordinary, 135-170 degrees: Uncolored or black arms; Orange or Red Glass Bulb.

Intermediate, 175-225 degrees: White arms; Yellow or Green Glass Bulbs

High, 250-300 degrees: Blue Arms; Blue Glass Bulbs.

There are more classifications, but one of these is always in a parking structure.


WHY IS THIS IMPORTANT?

Simple, for those of use who use a high BTU boiler inside a garage, you will find that the heat rise is substantial. With just 1 of our boilers on, we have managed to reach over 175 degrees at the ceiling level thus exploding the glass and have the fire sprinkler system activated. We have done this 3 times within the 21 years since we have been in business cleaning Parking Structures.

I suggest getting a Fluke 62 Mini Infrared Thermometer. They go for about $100. It is a necessary piece of equipment if you want to clean garages with extreme heat. ( Meaning above 160 degrees ).

Since we have bought 5 of them, One for each team leader, we have not had a problem with the sprinklers going off.
 